Much food for thought. It is my understanding that we ground every third pole to a ground rod or wrapped pole bottom to try to minimize the distance a fault path has from the downed conductor through the earth and up to the neutral. Agreed that down wire can remain energized due to low fault current, especially on snow or in rocky soil. But we have to try to minimize the time a conductor is down, because many areas up here are sparsely populated (second homeowners, etc.) so we don't usually know about outages until a customer calls. Been this way since long before I got here, so I guess that's what the engineers decided was the best solution. Smart metering will help with outage notification, but still a real problem. As far as recloser tripping, on three phase circuits we try to keep the loads balanced between phases. Trip settings are such that a single phase condition will hopefully cause enough imbalance to trip on a "ground" fault. Fuses are still the best on single phase taps. Summer settings are non-reclose with one fast trip. Better to have an outage than spark a forest fire. I think I'm gonna back out of this thread....probably getting into areas way beyond Code. Thanks for the "fun"! Have a gidday.