For a line side tap, should the neutral and EGC be connected at the fused AC disconnect, or remain separated (unconnected) until the main service panel?
Yes. :angel:For a line side tap, should the neutral and EGC be connected at the fused AC disconnect, or remain separated (unconnected) until the main service panel?
Yes. :angel:
This is an area where the code is ambiguous, pubic discussion by experts varies in conclusion, and, most important, AHJs differing what they require. The best answer at this time is to ask your inspector.
The line (supply) side disconnect of a PV system is in exactly the location that a clustered service disconnect would be installed if the PV system were a load.Please elaborate on why combining egc and neutral would be allowed at an ac disco. A code section (up to interpretation) would suffice. :angel:
Exactamundo. In San Antonio we are required to bond neutral to ground in the disco (and all that comes with that) but in Austin we are required NOT to bond N to G in the disco.The line (supply) side disconnect of a PV system is in exactly the location that a clustered service disconnect would be installed if the PV system were a load.
This supports the argument that there should be an EGC to neutral bond on the PV side of the disconnect.
But the code also says that the PV AC disconnect hardware does not have to be rated as a service disconnect, supporting the argument that there should not be an EGC to neutral bond there either.
I do not find either argument totally persuasive and sufficient to settle the issue.
Exactamundo. In San Antonio we are required to bond neutral to ground in the disco (and all that comes with that) but in Austin we are required NOT to bond N to G in the disco.
I think you will find in upstate NY working through NYSERDA on a supply side connection they want neutral to ground bond on the AC disco. Thus, making your former main panel a sub.
Please elaborate on why combining egc and neutral would be allowed at an ac disco. A code section (up to interpretation) would suffice. :angel:
The latter, of course.So electrons flow differently in different parts of the state of Texas? Or we just have an ambiguous situation that requires an arbitrary judgement call.
So electrons flow differently in different parts of the state of Texas?
Articles 230 and 250. Bonding the EGC system to the neutral at the service disconnect is what is normal. What is controversial is whether a PV disconnect on a supply side tap is considered a service disconnect.
The line (supply) side disconnect of a PV system is in exactly the location that a clustered service disconnect would be installed if the PV system were a load.
This supports the argument that there should be an EGC to neutral bond on the PV side of the disconnect.
But the code also says that the PV AC disconnect hardware does not have to be rated as a service disconnect, supporting the argument that there should not be an EGC to neutral bond there either.
I do not find either argument totally persuasive and sufficient to settle the issue.
NOT. AND ≠ OR...
Now that we're in Article 230, take a look at 230.71(A), specifically "The service disconnecting means for each
service permitted by 230.2, or for each set of service entrance conductors permitted by 230.40, Exception No.1,
3,4, or 5
Exception 5 is where we go next. It reinforces what was just stated, that we are dealing with a new service disconnecting means and set of service-entrance conductors.
...
Around here my experience is just the opposite. CPS in San Antonio is the only AHJ I know of in Texas who dictates that there be a G-N bond in the PV AC disco. I have no dog in this hunt; we have debated it until we are blue in the face but no argument however emphatically presented carries the day. It would be great if the NEC would explicitly state in 705 which way it should be. Even if it really doesn't make any difference, pick one already.There are two opposing camps on the issue of the supply side interconnection being a service entrance. That drives the AHJs to have different interpretations. Most I have talked to or heard from believe that the PV disconnect of a supply side interconnection is a service entrance and needs a service bond, but there are a few who believe otherwise.
So electrons flow differently in different parts of the state of Texas?
NOT. AND ≠ OR
Yes, the service side conductors are Service Entrance Conductors (SEC). There is no Code stipulation that a service disconnecting means must go on the end of an SEC.
Um, 230.70, General? Definition of service entrance conductors?
(I'm pretty sure that last time around you ended up arguing that they are not SECs because of the definition of a service. [EDIT: actually it appears you never really responded to my points on this.] )