packersparky
Senior Member
- Location
- Wisconsin
- Occupation
- Inspector
i do not see how it is concluded the NEC continuous without spicing the GEC is being applied incorrectly.
The illustration of GEC taps with multi and ganged service disconnects is specifically allowed in the NEC
and the grounding electrode conductor conductor is still required to be with out splice unless irreversible
And just for what it is worth i do not see a splice in the GEC or the bonding conductors bonding the grounding electrodes together in the illustration of the grounding electrode system that posted here in 27
The OP stated that inspectors are requiring that the GEC taps be connected to the GEC using irreversible means.