kwired
Electron manager
- Location
- NE Nebraska
How often is 3/8 rebar sufficient for structural codes? Seems if anything he should have rejected the 3/8 bar for structural reasons.Here in NJ you cannot pour the footings without a footing inspection which includes the installation of or connection to the CEE. I've probably mentioned this before but I did have a job where the footing inspector wouldn't allow the pour because there was no connection to the rebar. Turns out the rebar was 3/8" and didn't qualify as a CEE in the first place but he didn't care or didn't know the code. Someone had to run to Home Depot to buy a piece of #8 copper and a rebar clamp and install it before he would sign off. Since the rebar and the #8 were both too small I just left it off when we installed the new 200 amp service. I think that I might have actually cut it off.