Connection between Liquid tight and PVC

Status
Not open for further replies.

aelectricalman

Senior Member
Location
KY
I could not find a suitable connector to link PVC and Liquid-Tight, so I did this. I took a Liquid-tight connector and a female adaptor which has a PVC connector on the other end and linked it. Now, where the Liquid-tight connector links with the PVC connector, on the female side (where the threads are on the inside, the Liquidtight connector screws on to the PVC connector. Is this code compliant? Does anyone know of a better way. Thank you.

[ April 11, 2005, 10:04 PM: Message edited by: aelectricalman ]
 
Re: Connection between Liquid tight and PVC

It's a common way that I see hot tubs hooked up.

I prefer to have a pullbox instead of the female adapter transition, but I can't think of a violation with it.
 
Re: Connection between Liquid tight and PVC

However, the box connectors for liquidtight conduit have reduced cross section inside, particularly for nonmetallic variety.
 
Re: Connection between Liquid tight and PVC

Carlon sells liquid tight "flexible offsets".
It is just a 6" piece of 1/2" L.T. flex, with a L.T.connector & a 1/2" PVC female adaptor on each end!
It's important to thread the LT connector tight into the female adaptor so the rubber ring seals the connection, keeping it Liquid Tight.
;)
Dave
 