bobby ocampo
Senior Member
don_resqcapt19 said:The problem is that the connection to earth does not reduce the electric shock potential of the faulted equipment on solidly grounded systems.
There are different sources of electrocution. One based on the illustration shown which is the step potential and the other one is the energized metal piece. To solve step potential due to the energization of the earth because of a very high fault current, the resistance of the ground should be reduced by installing more ground rods near the energized metal piece or a ground mat connected to earth. This is the reason why I am comparing what is being done in a transformer substation. The reason why there are many ground rods installed in a substation is to reduce step potential if a person is inside the substation at the time of a very high fault current.
The connnection of the energized metal piece to earth is to reduce its potential to ground to reduce electric shock.
don_resqcapt19 said:It does do that under normal conditions for solidly grounded systems and under both single fault and normal conditions for ungrounded systems.
Reducing the energized metal piece to ground potential is applicable to all types of system (solidly grounded, HRG, Ungrounded System).
Step potential has a different solution to reduce electric shock. If fault current is very low such as in an Arcing ground fault or in HRG, then there will be less step potential. Step potential is equal to the resistance of the ground times value of the fault current.