bobby ocampo said:
winnie said:
But here is the kicker: without an earth electrode, this elevated voltage may be present without any sort of fault at all,
Non current carrying metal piece will not be energized unless there is a fault. The metal piece will have not potential to ground if there is no line to ground fault. Please explain how the metal piece will be energized without a fault.
If you have a piece of metal that is entirely isolated from the earth, then it may hold a charge relative to the earth and thus be at an elevated potential relative to the earth. No current flow is required; simply a charge on the metal.
A
single connection to an earth electrode will eliminate this 'static' potential.
bobby ocampo said:
Even at low current if this current carrying conductor touches the metal piece it will increase its potential to earth equal to line-to-neutral voltage of the system. This is a safe experiment you can measure the voltage to ground if the metal piece is not connected to earth.
If a current limited fault to
bonded metal occurs, then the potential of the metal will be raised, but only slightly. The voltage of the metal will not become the 'line to neutral' voltage, but will instead be raised by the voltage drop in the EGC system. Most of the line-neutral voltage will be dissipated in whatever is acting to limit the fault current. You have a series circuit, which includes the source (transformer or generator), the circuit conductors, the EGC system, and whatever limits the fault current. It doesn't matter if the current flow is limited by a grounding impedance or by something else, the net result is that the voltage of the bonded metal will be raised by the fault current * EGC resistance.
bobby ocampo said:
This is the comparison I am making for an arcing ground fault with a fault in HRG. Arcing ground fault like single line to ground fault in HRG has low fault current that the EGC despite its return path to the source will not operate the OCPD. Why? Because the fault is also low in an Arcing Ground fault. In line with this the metal piece will already be energized and if the EGC is not connected to earth will have a potential equal to line-to-neutral on a single line-to-ground arcing ground fault.
This is not correct. The limited current flowing in the EGC system will cause one portion of the system to be at
slightly elevated potential relative to other portions, in proportion to the current flow and the resistance. If any
single portion of the EGC system is connected to an earth electrode, all other portions of the EGC system will be at low potential relative to the earth.
bobby ocampo said:
The solution of installing additional grounding electrode is to solve the problem in the illustration of the post showing that there will be step potential from the post despite of the additional grounding electrode installed.
That understanding of the lamp post illustration is misguided. It is quite true that an
extensive grounding electrode system would eliminate the step potential hazard around the energized lamp post. However simply adding the code required bonding EGC would be more effecting and less expensive for eliminating this hazard. With the required EGC, then no additional grounding electrode is needed.
bobby ocampo said:
At a very high fault current based on the 1000KVA transformer at 5% impedance, the prospective fault current based on short circuit analysis on a single line to ground fault is 87% of the bolted 3phase fault. In this example, single line to ground fault will be 20,000 amps or 20kA. At the instant of the fault there will be a step potential which is hazardous if earth resistance is high. One of the solution to lower step potential is to install additional grounding electrode similar to what is done in a substation.
It is quite true that a bolted fault in a solidly grounded system can cause so much current flow that the potential of bonded metal will be raised significantly. However such a fault will quickly open OCPD. Additional grounding electrodes will not significantly reduce the potential of the bonded metal during such a fault condition, however sufficient grounding electrodes might serve to form an equipotential system and eliminate contact potentials. In this latter case, I contend that the safety benefit is the result of the metallic bonding of the equipotential grid, and not a result of the contact with soil.
-Jon