Mr. Ocampo,
You present a very confusing picture. On the one hand you show significant understanding of the technology. On the other hand, you keep making statements that appear to be physically incorrect, or which conflate very different situations.
Most of us involved in this discussion are considering conventional building services, including large 480/277V systems, possibly ungrounded or high resistance grounded, probably solidly grounded. If you are making your assessments from the point of view of utility distribution systems, then your very different perspective on very different systems may be part of our mutual misunderstanding. Please clarify the basis from which you are discussing things.
Carl asked you to state your assumptions and reasoning. I've asked you to show your calculations. Your continued pronouncements without stating their basis makes them neither correct nor incorrect, but simply meaningless.
Consider an isolated HRG system, consisting of a generator, building wiring system, equipment grounding conductors, grounding resistance, etc. The grounding resistance connects the generator neutral to the EGC system. If there were absolutely no earth electrode at all, then there is the possibility that the EGC system will be at elevated voltage relative to the earth. Clearly this risk of elevated voltage shows the importance of having some sort of earth electrode. But here is the kicker: without an earth electrode, this elevated voltage may be present without any sort of fault at all, and a low current fault will not in any way change the voltage between this hypothetical un-earthed EGC and the soil. In such a system, a single earth electrode is all that is needed, and there will never be sufficient current injected into that earth electrode to cause a step potential hazard.
Now consider a different HRG system, where the source neutral is connected to an earth electrode via the grounding resistance, but this is _not_ connected to the EGC system. In such a system, a fault to the EGC could place full line-neutral voltage on the EGC relative to soil. Question for you: in such a system, what could be done to reduce the potential on this EGC system?
I repeat to you: show your assumptions and describe the systems in which you are envisioning your examples. In all of the systems that I am considering, proper bonding reduces exposed dangerous voltages to extremely low levels or extremely short durations. In these systems, grounding electrodes beyond the initial required one do very little.
-Jon