ivsenroute
Senior Member
- Location
- Florida
If they connect to that CEE then they won't need any rods.
PS this is not my install, it is my inspection
PS this is not my install, it is my inspection
Yes I did say that the GEC to the rods was to be sized according to 250.66(B) which would be a #4 going to the rods and then on the the tail left for the CEE where a split bolt could be used.
Is this correct?
When daisy-chaining bonding jumpers one has to be careful. Rods are permitted to have #6 cu yet CEE requires #4 cu. This #4 cu would not be permitted to reduce to #6. 250.64(F)
Well that would depend on the size of the service entrance conductors. For a typical 150 amp service the GEC is only required to be #6 in the first place so you could have a #6 to the rods and the rebar.
Chris....on side note, would you consider the GEC connection to the main bonding jumper located in the section of a service that is sealed by the POCO as accessible? My AHJ says "no". I say "yes" because it is accessible without damaging anything but a couple of POCO seals.
I have always considered this type of install as accessible. I know some POCO's will not allow this connection to be made in their meter section though.
Chris
I know you'll be surprised to hear me say this (There is a major difference, the NEC specifically tells us that section is part of the electrode.
I did - HereAnd I can't believe I forgot to submit a proposal on this.![]()
Our local POCO (EMC) requires the GEC to be run thru the meter base AND up the mast out the weatherhead connecting at both locations. But Georgia power does not want it anywhere near their equipment. They even balk if you have bond bushings on their side of the equipment!
Why would they want a GEC in parallel with the neutral?
Cool.I did - Here