You need to get out of industrial application mode - these "constant pressure controllers" are for small domestic wells typically only up to 5 horsepower. The controls used before they started making these drives was just a direct acting across the line control method, with user seeing pressure vary from say 30 PSI at "cut in" up to 60 PSI at cut out. Now replace simple pressure switch and/or associated motor contactor with this constant pressure control scheme and you can set output for 45 PSI and unless you are calling for more demand then the pump can deliver - you pretty much get a fairly constant 45 PSI in the same system - plus you get soft start/stop and motor only runs at needed speed when demand is low.Well, we've been supplying VSD pump systems into the water industry for quite a few years. Most of these have been for water companies/authorities supplying potable water. Pumps in pumping stations pumping treated mains water - lots of it and quite often over long distances. The London Water Ring Main is 50 miles for example. One of the more important parameters they have to control is pressure - you don't want too many burst water mains under the streets of London......
Pressure is measured remotely from the drive. In the early days we had external PID controllers. Nowadays, a PID loop is often part of the drive internal package. The PID loop can be used to any measurable parameter including, but not exclusively, pressure.
Perhaps that goes some way to explaining why I think calling it a Constant Pressure VFD is a bit.........odd.
Can you use some other drive, a pressure transducer and set it up to work here - yes, these drives just happen to be packaged with only selected options/settings readily available to the user as they were only intended to be used for a fairly specific application instead of being considered a general purpose drive. Plus the well installers that typically sell them don't need to know much about drives in general, just follow set up instructions, most parameters you find on a general purpose drive they don't understand are already programmed in and are not something they have easy access to - just the typical parameters that may need changed for their more specific application.