Ed MacLaren
Re: continuous grounding conductor
In order to accomplish this, metal enclosures, conduits, and cable sheaths would have to be isolated from the earth, and everything in contact with the earth. That is clearly impractical.
As long as there is a "single connection" at one point in the GEC there can't be objectionable current flow.
It is much more practical to make the "single connection" at one point on the grounded (neutral) conductor, and isolate the neutral from ground thereafter.
The term "single point grounding" means that the GEC/GECs is/are connected to the grounded (neutral) conductor at one point within each facility.
The grounding electrode "system" can be comprised of any number of individual grounding electrodes, the more the better, as long as they are interconnected with the correct size wire.
Ed
[ April 14, 2003, 09:28 AM: Message edited by: Ed MacLaren ]
The term "single point grounding" does not mean that the Grounding Electrode Conductor (GEC) is connected to the earth at one point only.My definition of single point ground is single point ground (as in earth) not as in buss bars.
Ed