You're welcome. We went over such things as hole-sawing between panels to relocate generator circuits to one panel, how to fit one ATS and one disconnect in the wall-space, how to explain options to the customer, etc.
I recommended providing an estimate for a full-capacity system with a 400a ATS and 70-75kw genny, as well as a realistic system with only one panel serving loads that really can't wait for normal power to be restored.
I also suggested sitting with the customer and going over every circuit, and assign each to one of three columns: Definitely on the genny, Definitely not on the genny, and Optional depending on leftover capacity or space.
One thing I didn't bring up was the additional gas volume required for either size. A larger generator increases the likelihood that the existing gas line and meter will have to be up-sized to provide the necessary BTU for the genny.
Well, there's your 100a emergency capacity. You could either supply the 100a panel and avoid load-shedding if you can narrow down the generator list enough, or supply the 200a panel and incorporate load-shedding.