Just wondering if have been living in the dark ages. I work in an area that I have to keep up with 2005-2014 codes in different municipalities. I was turned down for the first time today for running a 6/2wg to a cook-top that is only rated 240v. Blk Wht and bare ground from the cook-top. Inspector says the feeder has to be a 4-wire. Can someone tell me where in the code I can find this requirement.
Thx
If the cooktop is rated 240v and not 240/120 then the inspector is incorrect. The code requires a separate equipment grounding conductor and neutral if a neutral is required. In the old days we could use the equipment grounding conductor as the equipment grounding conductor and neutral-- that is not allowed any more.