080911-1954 EST
ELA:
The small MOV is across the AC input points of the bridge rectifier, and also in parallel with the anode and cathode of the SCR. The resistance and inductance of the trip coil is in series with the bridge. And a capacitor is across the small MOV. This should provide fairly good transient filtering.
This is a rather neat design. First, is the MOV directly across the line, then a dropping impedance to the input of the bridge, another MOV, and a shunt capacitor. This should do a good job of protecting all the electronic components, and holding the dv/dt down. Obviously assuming the components are good and no excessively large input energy pulse occurs.
wptski:
A false trigger with long random times between occurances is tough to troubleshoot. Also is it really a false trip.
Does this tripping occur if there are no loads on the GFCI? If so, then are there any large transient generators in the home? 8 ft Slimlines produce large transients. Motors with mechanical relay contacts do also. Switched inductive loads. Is there anything noticeable occuring at the time of trip?
If there is a load on the GFCI, then possibly start looking for problems in the load.
The brand and year of manufacture and others experience with the same device might help provide background information.
Are there other GFCIs in the house that do not randomly trip?
Why does a machine repairman have a better knowledge of troubleshooting electrical problems and knowledge of instruments than many electricians?
peter d:
With the construction that I have seen I would expect wet environments are likely to cause problems in various areas of the device. This might be the reason Cooper has a conformal coating on part of the circuit.
.