(4) #4/0 and (1) #6 XHHW?compact fits in (1) 2" EMT.
Again why #6... Isn't this a 225 amp breaker?
(4) #4/0 and (1) #6 XHHW?compact fits in (1) 2" EMT.
Again why #6... Isn't this a 225 amp breaker?
Your calculation only calculated the area of the conductors and not the fill of the conduit.
You need to divide the conductor area by the conduit area to get the percentage of fill.
#6 is based on 200A OCPD size per art. 250. It is a common installation since 4/0 may be specified due to Voltage Drop. The reason why EGC wire is considered is that many engineers and indeed many internal specifications for clients, ranging from universities to defense contractors to military, call for an EGC wires (the merits of which, or lackethereof, have been discussed a considerable number of times on this forum and elsewhere). I'm pretty sure you've been involved in many of those threads so you should have a good idea of both sides of arguments for this practice![]()
per NEC 240.4B & 240.6 is it allowable to use 3/0 on a 225A ckt bkr? (for a non-continuous rated load).
I don't have to figure the percentage, I just can't exceed what is shown in the column of Table 4.
#6 is based on 200A OCPD size per art. 250. It is a common installation since 4/0 may be specified due to Voltage Drop. The reason why EGC wire is considered is that many engineers and indeed many internal specifications for clients, ranging from universities to defense contractors to military, call for an EGC wires (the merits of which, or lackethereof, have been discussed a considerable number of times on this forum and elsewhere). I'm pretty sure you've been involved in many of those threads so you should have a good idea of both sides of arguments for this practice![]()
It does exceed Table 4.
Table 4 for 2" EMT = 1.342
Area of conductors = 1.3455
You rounded your calculation down to 1.34
Also as Dennis stated, you cannot use this a 225a feeder without a #4 ground.
They are sitting on my desk at work.
From Table 4:
2 EMT area for more than 2 'wires' 1.342 sq in.
From Table 8:
4/0 THHN = 0.3237 * 4 = 1.2948
6 THHN = 0.0507
1.2948+.0507=1.34. :grin:
I did not round anything down, I simply calculated it to two places. How many places does the NEC require?
I still ask ......... where does it say I cannot calculate it this way.
I mentioned that way back in post 11. :grin:
If you have up the current carrying conductors for voltage drop you would still have to up the EGC one size so even with 4/0 on a 200 amp breaker you would still have a #4 EGC. so its 3/0 on a 200 with a #6 EGC max for existing conduit, or you use the conduit for the EGC.:roll:
But the OP states 3 phase 4-wire which I take as meaning 3 phase conductors and a neutral not an EGC?
I don't really see a reason in doing that. The current your conductor may carry is still limited by the OCPD and so is the fault current should a fault occur. Can you provide a reason why you would upside your EGC conductor in such a case?