kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
Yes, I know that. I addressing this point you made:
In practical terms, that load could be also be supplied with just three conductors from a star connected transformer with the neutral connected to ground at the transformer.
I've seen it here in UK on industrial applications.
But with the wye secondary you have four points on the system no matter what. I suppose you could choose not to use the center point but it is still there and still common to all three phases.
With a delta secondary you only have three points. If you choose to ground mid point of one phase you have four, but there is no requirement to ground the mid point of one phase. The coils do not even need to have the center tap, main reason they usually do on pole mounted transformer banks is because they are made with same transformers used for single phase systems, which are always in stock in the POCO parts yard/warehouse.