While other parts of the NEC allow the ground->neutral connection to be made in a few different places, it must occur at the 'utility service entrance' equipment. The This 'quirk' has been known to cause some confusion in regards to the requirements for Ground Fault on services.
Here, for LV residential services (400/230V) it is usual for the earth (grounding) to be done at the local distribution transformer. The is usually an 11kV delta to 400/230V star unit feeding a number of residences.
A slight aside....
The ROC made a visit our local transformer. I happened to he home at the time so I asked them what they were doing. They were replacing the neutral to ground connection with aluminium.
Thieves (pykies) had stolen the copper. A dreadful but not unique occurrence. Another similar crime is the theft of drain covers and manhole covers. They are cast iron and they are being stolen for their scrap metal value. Perhaps a sign of the economic times. Still doesn't excuse it in my book.
However, if the X0 (star point) is allowed to float, and never ever be referenced to ground, then it does not need to be taken to the service equipment. This type of utility provided ungrounded service is extremely rare, maybe to the point of being non-existent.
Floating is not good.
As you probably know, we do power electronics.
For AC to DC conversion on some larger systems we sometimes use 24-pulse rectification.
Two supply transformers, each with two secondaries. One star, the other delta. That gives a 30deg shift between the secondaries. The 15 deg shift between the two transformers is done on the primary. The primaries are delta with a bit sticking out from each corner of the delta. The bit sticking out is in different directions for the two transformers thus giving all the secondaries required for the 24-p rectification.
As I noted, floating is not good. But how to ground a system with multiple secondaries, all interconnected, isn't quite straightforward.
Our approach is to put a balanced voltage divider across the DC and tie the centre point to earth (ground) and then sense the voltage balance across each half.
We sell a version of this to some companies making traction rectifiers.