- Wisconsin
- PE (Retired) - Power Systems
The Orange box uses lighting contactors extensively to turn large transformers off and on loaded, but its not a motor load, but then the OP is not starting the motor until after the transformer is turned on. They have a couple thousand stores like this, and don't appear to have a problem with it, some stores are over 20 years old and use this system. When I first saw this set up, I thought they would be issues, but I never had to change one due to contact failure, it's always a coil failure.
Are you sure they are "lighting" contactors? Past 30A, the primary difference between contactor types, is the composition of their contacts. Some of the hardest loads to switch (from a contact perspective) are tungsten filaments.
For the OP's application, it is all about inrush current ratings, not full load ratings.