gar said:To further clarify in the CNC area where people are doing stupid things.
If the Equipment Grounding Conductor (I like to call it "safety ground wire" to help the average person understand its purpose) is disconnected at the CNC and in its place a ground rod is substituted, then effectively the earth path back to the main panel becomes the EGC. This is totally unacceptable because of the almost certainly high resistance.
A journeyman electrician will never do this
gar said:Even if the EGC is correctly installed to a CNC the addition of a supplemental ground rod at the machine only has a marginal effect on ground path noise. In other words it seldom solves the problem.
As journeymen electricians our emphasis for grounding (earthing) is an electrode system as defined in 250 part III, our emphasis for equipment grounding (bonding) is a system as defined in 250 parts V & VI. Grounding and bonding are summarized thoroughly in 250-4 again this is where are emphasis is.
A correctly wired building will not have noise. This means no parallel neutral paths, balance load respecting harmonics, no common neutrals, data/comm cabling space from voltage... Noise or stray current on non-current carrying items are most often avoidable. Existing installations with high noise will need qualified electricians to help qualified technicians clean up bad wiring/cabling because supplemental work is a Band-Aid not a repair.