Countertop receptacles on or above

retirede

Senior Member
Location
Illinois
Were they actually drilled on site or were they manufactured with the holes?

Jap>

Both. The 2 faucet holes were in there when they showed up at my house. They drilled the one for the air switch on-site. The finishes of the bores all looked identical so my guess is they were all drilled post-finishing.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Both. The 2 faucet holes were in there when they showed up at my house. They drilled the one for the air switch on-site. The finishes of the bores all looked identical so my guess is they were all drilled post-finishing.
Field drilling or cutting of stone is not difficult. I cut my granite countertop with a circular saw, diamond blade, and spray tank (to supply the water) to install a new cooktop that didn't fit in the old hole.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The way it's worded an outlet installed to serve the work surface must be above the work surface, yet there is no requirement to have one at all serving an island or peninsula, though provisions need to be provided to add one if ever desired to have one serving the counter top.

There is nothing that says you can not put receptacles on the side of the island or peninsula, they just don't count as serving the counter top - even if placed just below the counter top.

May not have been the intention but is what it says.
And you might be required to do so, if the island or peninsula counts as wall space. The task group was working on language to permit receptacles on the sides as long as they are at least 24" from the countertop.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
And you might be required to do so, if the island or peninsula counts as wall space. The task group was working on language to permit receptacles on the sides as long as they are at least 24" from the countertop.and why 24"?
With the current wording I agree with kwired, the original code change should have considered need for the additional code wording. And why 24"? Previous code versions required 12". 24" means that the receptacle will need to no higher then 12" above the floor.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
With the current wording I agree with kwired, the original code change should have considered need for the additional code wording. And why 24"? Previous code versions required 12". 24" means that the receptacle will need to no higher then 12" above the floor.
Most cooking appliances have a 24" cord, so that prevents the countertop cooking appliance from being plugged into the receptacle that is required by the wall space rule.
 

norcal

Senior Member
Most cooking appliances have a 24" cord, so that prevents the countertop cooking appliance from being plugged into the receptacle that is required by the wall space rule.
Right or wrong a short extension cord will take care of the problem, but my point is trying to "idiot proof" things is not going to work.
 

Elect117

Senior Member
Location
California
Occupation
Engineer E.E. P.E.
Kitchens are a relatively dangerous place. Between knives, stoves, hot pots, etc. I don't understand how this makes it any more safe than a stove top already is for a kid. Tamper proof receptacles is really the extent you can go to. If a kid can reach the fryer they could still hurt themselves.

Manufacturers can add stickers / labels that say DO NOT GRAB on the cable but some kids can't read. And some adults too.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Or you'll just have people putting in the receps after inspection.
Or never putting them in, which is what I did, and I have never been tempted to use an extension cord. Either way, it's a design issue. I think the rule that you only have to make provisions for a recept in the island is a good compromise.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
So 6" below the countertop and I just tell the inspector they didn't want any receptacles to serve the island countertop? I mentioned this a few months ago in another thread where the wording should say any receptacle below a given distance from the island countertop is NOT serving the countertop. The old code versions used 12" so it should give an explicit measurement.
Not all inspectors follow "Charlies rule" so if you can't convince them of what the book actually says, your options are

1. just do what they ask

2. go up the chain of command - but they may not necessarily recognize Charlies rule either

3. hire a hit man.

:)
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
With the current wording I agree with kwired, the original code change should have considered need for the additional code wording. And why 24"? Previous code versions required 12". 24" means that the receptacle will need to no higher then 12" above the floor.
They apparently don't want one that "serves the countertop" on the sides but never got it worded right the first time.
 

coffeebean

Senior Member
Location
Mercer County NJ
Not all inspectors follow "Charlies rule" so if you can't convince them of what the book actually says, your options are

1. just do what they ask

2. go up the chain of command - but they may not necessarily recognize Charlies rule either

3. hire a hit man.

:)
#3 is not funny especially if you're an inspector
 

jimport

Senior Member
Location
Outside Baltimore Maryland
Occupation
Master Electrician
I'm glad that were still under the 2020 NEC. I'll be putting in a new kitchen later this year and I'll be installing a receptacle at the each end of the island and the peninsula. I use the island receptacle about 4 or 5 times a week and I extremely dislike having pop-up type receptacle in the countertop.
I can't imagine the grief I would have gotten installing a popup on this counter.
 

Attachments

  • 20241104_204006.jpg
    20241104_204006.jpg
    1.3 MB · Views: 22

TwistLock

Member
Location
California
Occupation
Electrician
Most islands have seating and people like to charge their devices while eating/working there. If client doesn’t want a pop-up, you could see if inspector would allow installing a 120v supplied multi port USB ‘outlet’ (no 5-15Rs). If AHJ says yes, do it and tell client you won’t be changing it. If inspector says ‘no’ tell him you’ll supply multi port USB with Cat cable into box. He shouldn’t object to that and client might be pacified with what they use most.
 