Plumber at this house I'm doing says the gas will be Csst the original gas black pipe and meter that fed the house is still there and will be used.
I've never bonded to gas service let alone Csst.
Googling I see people go to the black pipe service.. Others go to the compression connector of the Csst.
This post mentioned something about jumping black pipe and Csst ( I think)
https://forums.mikeholt.com/showthread.php?t=169232&highlight=Csst+bonding
Reading says a minimum # 6. The water meter is right there. I should be able to go from that right?
If I can't add a clamp to the water pipe could I make the #4 long enough to go unspliced from the panel thru the water to the gas ? Or would a separate 6 have to go back to the inter system bond or panel ground bar?
If I need to bond the black pipe, Is the clamp special for black pipe?
Pretty sure the Csst clamps are special. If I need to bond the Csst connector, Are those clamps elec supply house stock or plumbing ?
Thanks for the help.
I want to be Csst qualified. :- )
I've never bonded to gas service let alone Csst.
Googling I see people go to the black pipe service.. Others go to the compression connector of the Csst.
This post mentioned something about jumping black pipe and Csst ( I think)
https://forums.mikeholt.com/showthread.php?t=169232&highlight=Csst+bonding
Reading says a minimum # 6. The water meter is right there. I should be able to go from that right?
If I can't add a clamp to the water pipe could I make the #4 long enough to go unspliced from the panel thru the water to the gas ? Or would a separate 6 have to go back to the inter system bond or panel ground bar?
If I need to bond the black pipe, Is the clamp special for black pipe?
Pretty sure the Csst clamps are special. If I need to bond the Csst connector, Are those clamps elec supply house stock or plumbing ?
Thanks for the help.
I want to be Csst qualified. :- )