It is important to know what cycle you are on. Ohio is on the 2009 IFGC.
View attachment 12390
Remember that it is the system that has to be bonded where 'it' enters the building, in my example, and not necessarily where the GES 'enters the building'.
It's a shame a product was produced that actually became a danger when installed. The NEC gas always bonded the gas pipe thru the branch circuit EGC but when gastite & Wardflex introduced their CSST it was unknown of the consequence lighting strikes had on thier products (pinholes). Now the Fuel gas code has written the bonding to be a min conductor size due to this mistake. The Wardflex CSST instructions below are similar to the gastite CSST instruction:
4.10 WARDFLEX? CSST ELECTRICAL BONDING
Direct bonding is required for all natural and LP gas piping systems incorporating WARDFLEX? CSST whether or not the piping system is connected to an electrically powered gas appliance. Direct bonding is included as part of the manufacture?s requirements for both single family and multi-family buildings. A person knowledgeable about electrical system design, local electrical code, and these requirements should specify the bonding for commercial applications. WARDFLEX? CSST installed inside or attached to the exterior of a building or structure shall be electrically continuous and directly bonded, by a qualified person, to the ground system of the building. The gas piping is considered to be directly bonded when installed in accordance with the following instructions:
? A bonding conductor is permanently and directly connected to the electrical service grounding system. This can be achieved through a connection to the electrical service equipment enclosure, the grounded conductor at the electrical service, the grounding electrode conductor (where of sufficient size) or to the one or more grounding electrodes used.
? A single bond connection is made to the building gas piping downstream of the utility meter or second stage regulator (LP systems), but near the gas service entrance (either indoors or outdoors) of the structure, or down stream of the gas meter of each individual housing unit within a multi-family structure. A ?daisy chain? configuration of the bonding conductor is permitted for multi-meter installations. A bonding connection shall not be made to the underground, natural gas utility service line or the underground supply line from a LP storage tank.
? The bonding conductor is not smaller than a #6 AWG copper wire or equivalent. The bonding conductor is installed and protected in accordance with the NEC.
? The bonding conductor is attached in an approved manner in accordance with NEC and the point of attachment for the bonding conductor is accessible.
? Bonding/grounding clamp used is listed to UL 467 or other acceptable national standards.
? The bonding clamp is attached at one point within the piping system to a segment of rigid pipe, a pipe component such as a nipple, fitting, manifold, or CSST fitting provided it is manufactured with an appropriate and Code listed material. The bonding clamp must be attached such that metal to metal contact is achieved with the steel pipe component. Remove any paint or applied coating on the pipe surface beneath the clamp. See Figure 4.41 for guidance. The corrugated stainless steel tubing portion of the gas piping system shall not be used as the point of attachment of the bonding clamp at any location along its length.
Gastite has announced they will discontinue the Gastite CSST product as they have produced only FlashSheild CSST. FlashSheild CSST only requires the bonding per sized by the branch circuit supply the appliance.
4.10 Electrical Bonding of Gastite?/FlashShield? CSST
a) Unlike Gastite?, there are no additional bonding requirements for FlashShield? imposed by the manufacturer?s installation instructions. FlashShield? is to be bonded in accordance with the National Electrical Code NFPA 70 Article 250.104 in the same manner as the minimum requirements for rigid metal piping. However, installers must always adhere to any local requirements that may conflict with these instructions.
Technically the electrician has done his job and the IFGC requires the mechanical contractor to install a larger bonding conductor & the mechanical inspector to enforce the code -- This is now all messed up IMO.