Hello again friends! I need to jack this thread, only to go back to the OP first question! I have just run across this SAME setup for a 208/120V 3 phase temple. I'm going to attach my line diagram of the setup, and a picture of the CTs in the CT Cabinet. What I am worried about was already alluded to here, that energy exported through the CTs will be logged as production and not consumption. I am not convinced the CTs are bi-directional.
I am not concerned on the legality or jurisdictions on interconnecting in the CT cabinet, simply if the laws of physics and electrons will properly register production vs consumption. I am not even sure if this is a CT model issue.
I do have an inquiry in with National Grid here in MA, but I know you guys know your shit so figured I'd see what the experts here thought as well.
Thanks!
-Alex
I am not concerned on the legality or jurisdictions on interconnecting in the CT cabinet, simply if the laws of physics and electrons will properly register production vs consumption. I am not even sure if this is a CT model issue.
I do have an inquiry in with National Grid here in MA, but I know you guys know your shit so figured I'd see what the experts here thought as well.