I agree with you, and will add often the current is coming from voltage drop on the MGN and is primary neutral current.For a service GEC, I would say nearly the opposite. It is normal, first of all. The lack of current on the GEC could actually be an indication that it isn't properly connected to an electrode, although it could just as easily be lack of load or poor conductance between electrodes and earth.
(For a separately derived system I would agree with you.)
Turn all load off (main breaker maybe) and if you still have current on the GEC it is current from outside your premises, you likely not going to be able to do anything about it unless it is at high enough level - but has to be convincing to POCO to determine they have a problem.
This is a primary reason we have all the equipotential bonding rules around swimming pools. Fairly low neutral to ground potential will show up in the pool areas and will be more of a problem for a person submerged in water to get across even pretty low potential, by bonding everything together the entire pool can be above earth potential yet user can't be across this and true earth, they only in contact with one potential just like a bird sitting on an isolated high voltage wire on poles doesn't get electrocuted.