IF that on ground is connected to a metal underground water pipe and only if it is then .3 amps is explainable, but not ok. We ground partly so that .3 amps that shouldn’t be there won’t flow through us.
I do “know” what I am talking about. I assume YOU compensate for the .1 amps on your meter when you take a reading, and you can tell whether current is flowing or not. If current is flowing on a GEC IT IS ALWAYS abnormal. And an indication something is wrong somewhere.
How is it no ok...around me where we have metal underground water piping system, it is typical to find 20% or more of the neutral current on the water pipe.
There is no hazard, but the water pipe and the service neutral are in parallel via the other service neutral in the area. The current will divide in inverse proportion to the impedance of the paths. The only time there will be a hazard is where the service neutral is open and you cut the water pipe and get between the two ends.
In a recent storm, a tree limb broke the neutral but not the ungrounded conductors. The area has a common metal underground water pipe system and the home owner did not even know there was an issue with the service drop because all of the neutral current was on the water pipe...none of the issues that you would normally associate with an open service neutral. It was that was for 2 or 3 days until the power company repaired the service drop.
There will
always be current on the GEC if that GEC is connected to a common metal water piping system and it is 100% normal. If there was no current on that GEC, that would be abnormal.