B&V Construction
- California
- Remodel contractor
The panel in the linked image is located in Oregon and was installed and inspected in 2012.  The homeowner has been experiencing nusiance trips on one breaker which prompted an investigation.
Panel
House has a meter socket and this is the only load center. At first glance inside the panel everything looks OK, though it would perhaps benefit from a little tidying. As expected the neutral and ground are bonded using the bonding screw and the earth ground (Ufer in this case) is typical for this type of foundation. I am a bit puzzled by the multiple paths to ground though. This is 200A service and I would have expected to see a single 4AWG copper GEC. Instead there are three 6AWG conductors. This is of course incidental to the nusiance trips, but my curiousity was piqued.
And... there's current flowing on all three. At the time of my measurement the load was about 10A on one bus bar and 5A on the other, resulting in 5A returning to the service neutral. Measured with a Fluke ammeter the current on the "left GEC" was about 0.3A and on the "right GEC" about 0.1A, as well as 0.1A on the "main" GEC. Now I'm aware that there's always going to be a difference in potential between the service neutral and the earth ground. It's also unsurprising that if there's current on any of the three then there will be current on all three of them as they're parallel paths from one electrode to another. I did not, however, expect to see this much current passing to ground.
Are the "left" and "right" GECs redundant (and if so, why would the original electrician have installed them)? Are there any issues with this grounding arrangement? Is there a threshold for current bleed to a GEC before it becomes a concern? Thanks!
			Panel