It does get clouded a bit in a situation like described here. The campus owns the transformers, but POCO is contracted to maintain them. This still kind of makes it POCO controlled equipment even though they do bill the customer for most anything done to it. It may come down to more technical details in contracts or service agreements to determine just what the service point actually is.Since transformer ownership changed 4yrs ago, it's not clear to me where your service point is now.
If it switched to the supply side of the transformers, your new equipment installation may not be a service.
Grounding and bonding requirements for feeders and SDS for whatever your current code cycle is would be more appropriate than those for a service.
We don't let anyone do work on energized equipment (other than troubleshooting, voltage testing or non-contact inspections with appropriate PPE) If if the work requires use of a tool on energized conductors or circuit parts, we shut it down first.
Sent from my iPhone using Tapatalk
But if transformers are indeed on customer side of service point then the service equipment is going to be medium voltage equipment - if such service equipment doesn't exist we have an even bigger can of worms - plus now OP's building is served by two feeders instead of two services - which is a little more clear of a violation then if it were two services - maybe, there is another current thread debating multiple feeders and services to a building and whether it is allowed.
There is no bonding jumper at the generator where this CT is. Cant bond it here because the neutral is not switched. Yeah about the six disconnects i agree, just a poor way of doing things. I cant isolate the service wires to make any changes. I really don't like this method of wiring.
You have alternate path somewhere on load side of this CT or you would not lose any current before it reaches the CT causing the imbalance that makes it trip. Maybe an inadvertent neutral - ground bond somewhere? Doesn't have to be improperly installed jumper, just a skinned neutral touching a grounded object could do it. If this is serving a lot of data equipment - don't overlook someone thinking a ground rod was or a bond to a water pipe or building steel isn't a point of crossover causing such problems, and someone though this was a good solution to a problem at some point.