Don:don_resqcapt19 said:Bill,
No matter what the resistance is, the current will follow ohms law. It would not be unusual to get a megger reading of over 100 meg for an appliance. A 100 meg would result in a leakage current of 1.2 micro amps. Your meter has a resolution of 10 times that with a plus or minus 5 count accuracy. I guess the only way to continue is if we know the resistance of all of the possible leakage paths.
Don
We're making gains, as we've got away from the zero current statement. A couple of posts above I said that the 565 won't read lower than .01ma. Even with those specs, that isn't much current flow. Would you consider current flow below .01ma a problem? What would you consider a problem?