Im not sure on what degree any of this is normal and if its something I need to refer to someone at our shop with more experience.
Yesterday I had to replace a jumper around a water meter in a house.
I put my clamp meter on the GEC and the water pipe prior to the meter and I was getting somewhere in the range of .50-.75 ... so less than an amp. Nothing on the other side of the meter nor on any of the water pipes.
At the meter socket outside, they had a new ground rod sunk, the old ground rod was disconnected but next to it. I was not getting any current at the new ground rod however, I was getting about 1 VAC between the old a new rod.
Inside the house I went around clamping the various conduits (all emt) and some of them were also showing current in the the same less than an amp reading. Turning off any of those circuits had no effect on the reading. I also noticed the reading on the conduits fluctuated a bit from 0 to almost 1A in the span of the hour I was there. When the homeowner used a microwave in the kitchen, the readings on the conduit and the gec also fluctuated ... never going about 1A.
I was perplexed as usual and not sure if I am seeing phantom voltage or something else and was concerned there was a neutral issue at play here. A little reading online suggests some of this is normal but I am unclear as this is the first time I ran into something like this in the field.
Does this sound like an issue needing further investigation?
Yesterday I had to replace a jumper around a water meter in a house.
I put my clamp meter on the GEC and the water pipe prior to the meter and I was getting somewhere in the range of .50-.75 ... so less than an amp. Nothing on the other side of the meter nor on any of the water pipes.
At the meter socket outside, they had a new ground rod sunk, the old ground rod was disconnected but next to it. I was not getting any current at the new ground rod however, I was getting about 1 VAC between the old a new rod.
Inside the house I went around clamping the various conduits (all emt) and some of them were also showing current in the the same less than an amp reading. Turning off any of those circuits had no effect on the reading. I also noticed the reading on the conduits fluctuated a bit from 0 to almost 1A in the span of the hour I was there. When the homeowner used a microwave in the kitchen, the readings on the conduit and the gec also fluctuated ... never going about 1A.
I was perplexed as usual and not sure if I am seeing phantom voltage or something else and was concerned there was a neutral issue at play here. A little reading online suggests some of this is normal but I am unclear as this is the first time I ran into something like this in the field.
Does this sound like an issue needing further investigation?