Thanks so much for all your replies, its a real treasure of info.
In regards to those other readings at the incoming water line. I immedietly wrote that off as being normal since its a city water supply in parallel to the tx.... I just want to confirm that is safe to dismiss that as normal.
Testing the 3/4" copper as it enter the foundation a few inches from the actual electrode which yielded no reading....
With power on to the building under no load it was showing very low about .30 of an amp. With power off to the building that figure didn't change. What I forgot to mention with the main on to the building, when a large load was applied (in this case the heatgun again) the current on the water pipe leaped up to around 1 to 1.5 amps. It did not matter which circuit the load was plugged into.
These readings were observed immediately where the pipe enters the foundation. Checking the actual GEC yielded no results just a few inches from the actual entrance to the pipe and of course no where after the water meter was any of this observed.
Does that seem out of the ordinary?
Where I learned that some current on a GEC is normal it was the fluctuation when a load was applied that prompts me to inquire now.
2. The neutral in parallel (following a different conduit path!) could easily cause the readings you saw with the heat gun. Probably no relation at all to the other EGC/GES related currents you are looking at though.
In regards to those other readings at the incoming water line. I immedietly wrote that off as being normal since its a city water supply in parallel to the tx.... I just want to confirm that is safe to dismiss that as normal.
Testing the 3/4" copper as it enter the foundation a few inches from the actual electrode which yielded no reading....
With power on to the building under no load it was showing very low about .30 of an amp. With power off to the building that figure didn't change. What I forgot to mention with the main on to the building, when a large load was applied (in this case the heatgun again) the current on the water pipe leaped up to around 1 to 1.5 amps. It did not matter which circuit the load was plugged into.
These readings were observed immediately where the pipe enters the foundation. Checking the actual GEC yielded no results just a few inches from the actual entrance to the pipe and of course no where after the water meter was any of this observed.
Does that seem out of the ordinary?
Where I learned that some current on a GEC is normal it was the fluctuation when a load was applied that prompts me to inquire now.