Do not go by visual or Ohm Meter readings. The correct way to tell is to make sure there is a good amount of load current on the Sub Panel and then measure the voltage between N-G buss bars. If you see ZERO VOLTS then you know for certain it is bonded very close by. If isolated you should see some voltage up to 1 or 2 volts. Depends on the length, size of feeder cables, and current. Current clamping of the EGC feeder cable will also tell the story as you will see about equal current on both N and G feeder cable.note the sub in question is 3 wire feeder with rigid between main panel and subpanel to a detached building with its own ground rod. No bond screw visable on neutral bus.