Frank D
Member
- Location
- Los Angeles, CA
- Occupation
- Electrical project manager
I posted this on the Grounding and bonding section, but I wanted to open it up to a wider discussion. We have a client with a facility that has two. 277/480v 3,000 services. Each Service is fed by a separate utility company transformer that supplies this building only.
Everything in the electrical system is original from the engineering. It’s a hotel with restaurants, a spa and other amenities large facility. The engineering is excellent and the distribution system remains intact and it does not apparently have any modifications or anything added.
We have measured 25 A of current on the GEC on one of the 3000 amp services. This service provides most of the single pole loads throughout the facility whether they are 277 or 120. The other service only has 1.5 A on the GEC is mostly two pole and three pole loads, which makes sense since all of the unbalanced currents usually come from single pole loads.
I was under the impression that the GEC should never have any significant current on it, yet with this large of a service, and it being a wye system, I can see where some current of the unbalance would flow in the ground conductor with that large of a load
Everything in the electrical system is original from the engineering. It’s a hotel with restaurants, a spa and other amenities large facility. The engineering is excellent and the distribution system remains intact and it does not apparently have any modifications or anything added.
We have measured 25 A of current on the GEC on one of the 3000 amp services. This service provides most of the single pole loads throughout the facility whether they are 277 or 120. The other service only has 1.5 A on the GEC is mostly two pole and three pole loads, which makes sense since all of the unbalanced currents usually come from single pole loads.
I was under the impression that the GEC should never have any significant current on it, yet with this large of a service, and it being a wye system, I can see where some current of the unbalance would flow in the ground conductor with that large of a load