Cutting neutral and 220ing shared circuit

Status
Not open for further replies.
Hi I was hoping someone could explain to me how when you are sharing a neutral on a branch circuit and you cut that neutral without deenergizing the shared circuit why are you susseptable to backfeeding on the other ungrounded conducter. I understand that it happens I just don't understand the technical reason why.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
It's because the two loads are now in series and each load will see a different voltage drop across it based on it's resistance. The current will be the same through both loads. Two equal loads will share the total voltage equally. For a 208 volt system two identical loads will have 104 volts across them. For a 240 volt system the two loads will have 120 volts across them.
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
Hi I was hoping someone could explain to me how when you are sharing a neutral on a branch circuit and you cut that neutral without deenergizing the shared circuit why are you susseptable to backfeeding on the other ungrounded conducter. I understand that it happens I just don't understand the technical reason why.

Power is going into the shared circuit. It will travel through a load and look for a return path to the source. Hence, energized grounded conductor.
 

nakulak

Senior Member
draw it out on a piece of paper

plug on left is fed from left with a phase

in middle is juction box with neutrals

plug on right is fed from right with b phase

cut neutral going to panel, and you have a phase on left plug, former neutrals connecting the two plugs are now just a jumper, and b phase on right, so now you have the two plugs fed with 220. make sense ?
 