growler
Senior Member
- Location
- Atlanta,GA
I equate tests like this with HI's using fancy testers to test for voltage drop. They plug in their new tool and press the button which reveals at full load that receptacle on the other side of the house has a 6% VD. IMO it's kind of meaningless unless the testing could find a bad connection or something that may end up as dangerous.
IMO this often is nothing more than a pissing match with the EC trying to prove they are smarter than the HI.
The only time I have ever gotten into a "pissing" match with a home inspector was over voltage drop calculations.
First off the HI was useing a cheap off-brand analyzer that he had purchased through a class he was taking for home inspectors. He didn't even understand the concept of voltage drop or how to calculate. All he knew was how to plug in his gadget and he didn't even read the instructions for that.
I purchased the top of the line circuit analyzer for that time ( Ideal) and did read the instructions. This reduced the amount of voltage drop by a considerable amount but still over the 5%. I then measured the distance form the panel to the first receptacle and then to the rest of the receptacles involved and calculated the voltage drop manually. Sure enough the tester was almost perfect ( hard to get an exact measurement of cable in walls ).
After doing all the test and even having the head electrical inspector for the county give this guy a call and explain the 5% VD is a recommendation the HI would still not listen.
This was a cheap little town home and the wiring was as good as it gets. The owner could not afford to rewire the place just to please a home inspector and there was nothing that an experienced electrician or code inspector would have written up.