"All GFCI outlets when tested broke power too slow to meet current standards. Current standard is to break power within 25-30 milliseconds after being tested with a 7.5 milliamp load. All GFCI in the home broke at 115-164 or more milliseconds. Need to remove and replace existing GFCI outlets with new GFCI outlets"
Anyone have a reference for this requirement?
Folks we have gotten away from the original question here. I'm not really sure what to do in this situation. Some say just change them and be done with it and it does appear the HI has caused a bit of confusion on the part of the buyer.
I really didn't know that anyone was going around measuring the trip time of GFCIs or that there was equipment for the average joe that could do this. Still not sure how accurate this test equipment is ( they sell used one's on Amazon).
I have checked and Hubbell does state the trip time for their GFCIs is 25 Milliseconds and this seems to be what the HI is wanting.
I like a good fight but I think this might just take to much time so I would give the homeowner a price to change the GFCIs out to the highest quality and see what they wish to do.
I still think the Home Inspector is wrong to use this test equipment unless it becomes some sort of industry standard. If it does become a standard there should be a calibration proceedure to make sure the equipment is functioning properly and that the person useing it is properly trained.