It may be coming, but there are several problems along the way to be considered:Has anyone here done any DC wiring in a home with panel and breakers for lighting? Now that renewable energy along with LED lighting is getting way more popular I would think its a matter of time before people start doing something like this.
In renewable energy forums (solar PV in particular) people keep proposing a DC wiring network serving loads to avoid the need for an inverter, but few if any people end up trying it.
Yes, out at my cabin. Battery bank is 24V. I used QO CBs and panel. Works great.
Also used QO CBs and panel for the inverter fed 120VAC.
ice
RV's and campers have used 12 volt lighting and lower wattage equipment for years, but users still prefer to connect to AC source whenever possible so they can run higher wattage appliances, or have more lighting, the LED's we have today take another step toward being able to use the lower voltage for general lighting though.
How do you know the QO's will trip at their rating with 24 VDC?
I see two questions here, which one are you asking?How do you know the QO's will trip at their rating with 24 VDC?
1. How do you know that the QOs will have the same current sensitivity (thermal and magnetic) for 24V DC that they do for AC?
2. How do you know that when they trip they will successfully interrupt the current?
(PS: I would guess that in addition to the maximum nominal current rating, the interrupting rating for DC will be substantially different than the value for AC. So you also need to do a separate available-fault-current calculation for your DC source. That said, likely DC sources will be current limited to a far higher degree than a POCO transformer or even a generator.)
That question has had some reply, but why would a current responding device care about voltage? Now GFCI or AFCI units need a specific voltage to drive some of the logic components but not a straight thermal magnetic device. The issues of voltage with such devices is max voltage from an insulation breakdown point of view or arc extinguishing abilities of the contacts when they open - which will be higher for DC current than AC current @ same voltage level anyway.How do you know the QO's will trip at their rating with 24 VDC?
I agree runs would typically be shorter, but not always limited to short enough distances that voltage drop would never be a concern.RVs and campers don't need runs longer than a few feet. That's not the case in a home, which complicates LV DC design matters somewhat.
Why do think they would be lying?Catalog says they are rated for 48VDC and 5KA. Hopefully they aren't lying.
ice
don't forget - up to 5kABecause they are listed for use on DC up to 48v.
Not saying it wouldn't be acceptable to use there, but 90.2(B)(1) says the NEC doesn't apply to watercraft, and I'm not sure if there is a code that would apply to watercraft. Chances are there are standards that do apply but are not as well known and enforced as NEC is for other applications.I had a leg up. I ran in to SQD QO panels in DC service thirty years ago, when living in Southeast Ak. There is a large fishing fleet and a lot of the medium sized boats (30' - 60') use QO panels on their 24V systems. Easy jump for me to select one for my cabin DC service. (But I did check the ratings first :thumbsup
If I had not used QO, I likely would have gone with 32VDC ATO fuses and screw terminal fuse blocks. Although, that would have been a pain terminating solid #14 or #12 CU - I used romex. I never thought this one clear through.
And I did connect +12, 0V, -12 (ungrounded). I'm still not sure this was a great idea - it takes 2pole CBs for the 24V loads.
ice
Not saying it wouldn't be acceptable to use there, but 90.2(B)(1) says the NEC doesn't apply to watercraft, ....