For de rating purposes, is the neutral in a dryer circuit counted as a CCC?
And if so, and after de rating, the ampacity is 28 amps, must the wire be up sized or would a 30 amp breaker qualify as the "next size up"?
Additionally, since it is a dedicated load, could the actual load be used for the wire size calculation instead of going to #8?
This is a commercial application.
Thanks.
And if so, and after de rating, the ampacity is 28 amps, must the wire be up sized or would a 30 amp breaker qualify as the "next size up"?
Additionally, since it is a dedicated load, could the actual load be used for the wire size calculation instead of going to #8?
This is a commercial application.
Thanks.