Jim W in Tampa said:put a breaker lock on it.
Jim did you buy a truckload of breaker locks?
You sure are pushing them, can I get a quantity discount?
Jim W in Tampa said:put a breaker lock on it.
al hildenbrand said:I love this one.
Light on = OFF
Light off = ON
The perversity of that goes to my point.
![]()
The light is not mentioned in 404.7. . .The "up = ON" is. No mention of text as indication is in 404.7.Jim W in Tampa said:And just how will the service man know the light means off and not on ?
hey watch it....its only tainted on jims side of the bridge ...right jim77401 said:We have a winner!
Do you think the water is tainted in Florida? LOL
JK
Cavie said:breaker lockouts are very common in Sw Florida. At least three in every panel. Wh, DW, AH
iwire said:Jim did you buy a truckload of breaker locks?
You sure are pushing them, can I get a quantity discount?
big vic said:We use breakers with locks for disconnects for residential water pumps all the time. Never had an inspector question it.
mxslick said:I thumb my nose at the NEC on this one!!
Oh yeah, in my apt. I have a 20 amp rated Decora on my disposal (which is hard wired) and have never had a problem figuring out if it was "off" or "on".![]()
In the McMansions I frequently work on ALL devices are Decora!! (Including the disposal switch in the kitchens.) I don't think someone who paid millions for the design of his/her home is gonna change the disposal switch to a toggle just to satisfy a draconian provision of the Code.
Like the AFCI caper, I forsee a lot of switches being changed after the inspection because of this stupidity.
iwire said:Is the breaker within sight of the pump?
The fact that we do something all the time does not in anyway prove it meets code.
The NEC requires motors larger than 1/8 HP to have an indicating disconnecting means within sight.
Dude its not the code it was one inspector that had a bad day because he couldnt get a H-on the night before.mxslick said:If the Code has such a h-on about the fact that Decoras aren't "indicating" then they need to go the extra mile and prohibit them for all uses!!
big vic said:The pumps are usually at least 50' from the house and down the well casing 100' below ground
430.102(B) Motor. A disconnecting means shall be located in sight from the motor location and the driven machinery location. The disconnecting means required in accordance with 430.102(A) shall be permitted to serve as the disconnecting means for the motor if it is located in sight from the motor location and the driven machinery location.
Exception: The disconnecting means shall not be required to be in sight from the motor and the driven machinery location under either condition (a) or (b), provided the disconnecting means required in accordance with 430.102(A) is individually capable of being locked in the open position. The provision for locking or adding a lock to the disconnecting means shall be permanently installed on or at the switch or circuit breaker used as the disconnecting means.
(a) Where such a location of the disconnecting means is impracticable or introduces additional or increased hazards to persons or property
(b) In industrial installations, with written safety procedures, where conditions of maintenance and supervision ensure that only qualified persons service the equipment
430.102 Location.
(A) Controller. An individual disconnecting means shall be provided for each controller and shall disconnect the controller. The disconnecting means shall be located in sight from the controller location.
jwelectric said:Is it possible that 422.32 is addressing an appliance that has a ?MOTOR? and 422.31 is addressing an appliance that does not have a motor but is ?RATED? in horse power?
The answer as I see it is simple, if it has a motor a disconnect is required to be in-sight and it is to be indicating.
All the time. On every new house in Delaware, you are required to have at least one of these beasties in your panel, for the dedicated smoke detector circuit! We do lots of modular home hookups, and they have breaker locks installed on the water heater, furnace, dishwasher, and A/C circuits much of the time.77401 said:This should be a poll but has ANYONE everused or known anyone to use a breaker lock? on a residential job?
NOT ME!
marinesgt0411 said:If you want to keep it a decora switch just get a lighted decora switch light on its off light off its on to me thats indicating. ....
DaveBowden said:Back to the OP, the decora switch would have been allowable if there was either a cord & plug connection under the sink or if there had been a standard single pole switch under the sink or if there had been a lock out on the circuit breaker feeding the branch circuit ( it would not need to be in sight of the disposal under 422.31(B) because the word "or" is used in the article). 422.31(B) is what required the disconnect. 422.35 is what requires the ON/OFF indication. (As per the inspector.)
422.32 Disconnecting Means for Motor-Driven Appliance.
If a switch or circuit breaker serves as the disconnecting means for a permanently connected motor-driven appliance of more than 1/8 hp, it shall be located within sight from the motor controller and shall comply with Part IX of Article 430.
Exception: If a motor-driven appliance of more than 1/8 hp is provided with a unit switch that complies with 422.34(A), (B), (C), or (D), the switch or circuit breaker serving as the other disconnecting means shall be permitted to be out of sight from the motor controller.