Defintion of a motor rated switch

Status
Not open for further replies.

shortcircuit1

Senior Member
Location
USA
I am confused with the purpose of a motor rated switch. Lets say if you have a 1/2hp 120v. Can you use a normal 20a toggle switch? Whats the difference between a regular lighting toggle switch and a motor rated switch?
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
I am confused with the purpose of a motor rated switch. Lets say if you have a 1/2hp 120v. Can you use a normal 20a toggle switch? Whats the difference between a regular lighting toggle switch and a motor rated switch?

As an estimator I deal with it this way: Unless they specify a manual motor starter without overloads, or give a part number I consider it to be a Motor-circuit switch per the NEC definition. In order to use a snap switch as a motor disconnect it has to be horsepower rated. 430.109. Standard commercial grade and industrial grade switches have a horsepower rating.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
As an estimator I deal with it this way: Unless they specify a manual motor starter without overloads, or give a part number I consider it to be a Motor-circuit switch per the NEC definition. In order to use a snap switch as a motor disconnect it has to be horsepower rated. 430.109. Standard commercial grade and industrial grade switches have a horsepower rating.
The difference is, it's cheaper to make a switch with a 20A rating for purely resistive loads, but switching an inductive load like a motor means the switch must be capable of interrupting and extinguishing the arc that forms as the inductor tries to keep the current flowing. But just saying "Commercial grade" "Industrial grade" or even "Spec grade" does not necessarily mean you get that motor rating, you must look for it to be explicitly stated on the switch or the spec sheet. For example Leviton Spec Grade 20A toggle, yes, it's rated for up to 1HP. P&S / LeGrand Spec Grade 20A toggle, no HP rating at all.
 

shortcircuit1

Senior Member
Location
USA
The difference is, it's cheaper to make a switch with a 20A rating for purely resistive loads, but switching an inductive load like a motor means the switch must be capable of interrupting and extinguishing the arc that forms as the inductor tries to keep the current flowing. But just saying "Commercial grade" "Industrial grade" or even "Spec grade" does not necessarily mean you get that motor rating, you must look for it to be explicitly stated on the switch or the spec sheet. For example Leviton Spec Grade 20A toggle, yes, it's rated for up to 1HP. P&S / LeGrand Spec Grade 20A toggle, no HP rating at all.

Thanks Jraef.If i understand you correctly its the cost and the contacts for the motor rated switch that makes the difference between a simple toggle switch and a motor rated switch?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
The physical difference in the switch design is that horsepower rated switches have contacts designed to carry the high inrush current of motor starting as well as interrupt the inductive running current of a motor when opening.

Sent from my XT1585 using Tapatalk
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
The difference is, it's cheaper to make a switch with a 20A rating for purely resistive loads, but switching an inductive load like a motor means the switch must be capable of interrupting and extinguishing the arc that forms as the inductor tries to keep the current flowing. But just saying "Commercial grade" "Industrial grade" or even "Spec grade" does not necessarily mean you get that motor rating, you must look for it to be explicitly stated on the switch or the spec sheet. For example Leviton Spec Grade 20A toggle, yes, it's rated for up to 1HP. P&S / LeGrand Spec Grade 20A toggle, no HP rating at all.


I had a little trouble finding this but this is from legrand tech support I think you will find that virtually every switch is actually motor rated or every residential contractor that puts a residential switch in a bathroom with a fart fan is violating code.

[COLOR=#2C2C2C !important][FONT=FFDINWebProMedium !important]Thank you for your question regarding Pass & Seymour switch(Model # CS20AC1W).[/FONT][/COLOR]
[COLOR=#2C2C2C !important][FONT=FFDINWebProMedium !important]This Commerical grade switch is UL20 listed for 1HP at 120V and 2HP at 240/277V.[/FONT][/COLOR]
[COLOR=#2C2C2C !important][FONT=FFDINWebProMedium !important]Pass & Seymour products 1.800.223-4162 opt 3 Mon - Fri: 8am - 8pm EST (excluding holidays)[/FONT][/COLOR]
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
I had a little trouble finding this but this is from legrand tech support I think you will find that virtually every switch is actually motor rated or every residential contractor that puts a residential switch in a bathroom with a fart fan is violating code.

[COLOR=#2C2C2C !important][FONT=FFDINWebProMedium !important]Thank you for your question regarding Pass & Seymour switch(Model # CS20AC1W).[/FONT][/COLOR]
[COLOR=#2C2C2C !important][FONT=FFDINWebProMedium !important]This Commerical grade switch is UL20 listed for 1HP at 120V and 2HP at 240/277V.[/FONT][/COLOR]
[COLOR=#2C2C2C !important][FONT=FFDINWebProMedium !important]Pass & Seymour products 1.800.223-4162 opt 3 Mon - Fri: 8am - 8pm EST (excluding holidays)[/FONT][/COLOR]
Well, they can say it all they like but if they don't list that in their on-line specification sheets, or unless it actually says it on the switch body itself, it may as well not be true. An AHJ would want to see proof. Poor marketing if you ask me...
https://www.legrand.us/api/legrand/...h=/passandseymour/switches/hard-use/csb20ac4w
 

Besoeker

Senior Member
Location
UK
The difference is, it's cheaper to make a switch with a 20A rating for purely resistive loads, but switching an inductive load like a motor means the switch must be capable of interrupting and extinguishing the arc that forms as the inductor tries to keep the current flowing. But just saying "Commercial grade" "Industrial grade" or even "Spec grade" does not necessarily mean you get that motor rating, you must look for it to be explicitly stated on the switch or the spec sheet. For example Leviton Spec Grade 20A toggle, yes, it's rated for up to 1HP. P&S / LeGrand Spec Grade 20A toggle, no HP rating at all.
Yes. We would differentiate them as AC1 (pf > 0.96) and AC3 typically for induction motors.

From Schneider:

AC-1 category
This applies to all AC devices (loads) with a power factor of at least 0.95 (cos phi greater than or equal to 0.95).
Example of use: resistive load, heating, distribution.


AC-3 category
This applies to squirrel cage motors where breaking occurs while the motor is running.
Example of use: all squirrel cage motors, lifts, escalators, conveyors, bucket elevators, compressors, pumps, mixers, air conditioning units, etc.

The AC3 current rating is less/very much less than than the AC1 rating for the same device.
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent

shortcircuit1

Senior Member
Location
USA
Thanks everyone for your input. Now lets say if you have a cassette or an MCU in the ceiling. These are very low power consumption motors like 60-100w. Per code we need to have a disconnecting means with in sight. For that purpose would you put a normal 15 or 20a toggle switch or would you still use a motor rated switch for this kind of fractional horse power motors?
 

kwired

Electron manager
Location
NE Nebraska
Thanks everyone for your input. Now lets say if you have a cassette or an MCU in the ceiling. These are very low power consumption motors like 60-100w. Per code we need to have a disconnecting means with in sight. For that purpose would you put a normal 15 or 20a toggle switch or would you still use a motor rated switch for this kind of fractional horse power motors?
I think I know exactly what you are talking about and I have connected such systems before. You do not need a disconnecting means within sight, as they are under 300VA/1/8 hp, the branch circuit device is the disconnecting means.

They do not fall under art 440 either, only the compressor unit does.
 

shortcircuit1

Senior Member
Location
USA
I think I know exactly what you are talking about and I have connected such systems before. You do not need a disconnecting means within sight, as they are under 300VA/1/8 hp, the branch circuit device is the disconnecting means.

They do not fall under art 440 either, only the compressor unit does.


Understood.Thanks for the code reference.
 