due to an existing 100a sub panel fed by a 100a auto transfer switch, the inspector wants a panel schedule with demand loads for this panel, how do i do come up with the demand loads
because there is a 100 a sub panel that is fed by a 100 a automatic transfer switch, he wants a panel schedule with demand loads. So his concern is what?... that the sub panel's load is more than 80 amps continuous? Or that the feeding panel is overloaded? Or that the generator is too small?. You need to know what he's concerned about .
You're going to have to identify the loads. Any load that will be there for more than 3 hours is continuous. Any loads that will likely not appear together do not need to be added together... for example, you wouldn't think you'd have air conditioning and heating on at the same time. Any loads that CAN'T be turned on at the same time because of the way they are wired, don't need to both be added... just the largest.
Once you find out what he's concerned about, I think you ought to be able to satisfy the inspector yourself, without an engineer..