Derate 4/0 feeder

Status
Not open for further replies.

daiashi

Member
Location
NC
In my area in nc, inspectors are calling people using the spaces
on an outdoor 200amp disconnect to feed anything but the indoor
loadcenter.Ex. branch circuit to a heatpump.If the available spaces
outdoors are used then you have to derate the indoor feeders.Any ideas?:)
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
In my area in nc, inspectors are calling people using the spaces
on an outdoor 200amp disconnect to feed anything but the indoor
loadcenter.Ex. branch circuit to a heatpump.If the available spaces
outdoors are used then you have to derate the indoor feeders.Any ideas?:)
this can mean that T.310.15(B)(6) does not apply since it doesn't carry the entire load of the service. Is that what you mean?
 

Buck Parrish

Senior Member
Location
NC & IN
I think it has some thing to do with 310.15(b)6
I am not sure derate is the proper terminology in this case.
It is the new ampacity's allowed .
It's a pain , heh?


Okay Dennis beat me.
 

daiashi

Member
Location
NC
Thats the best idea I can come up with.By using the outdoor buss,
you are no longer allowed to use 310.15(B)(6) but 310.16.This
sound correct?
 
Status
Not open for further replies.
Top