What's the sizing method for sleeving NM cables in 2" sch.40 pvc conduit ,that's 24" long going in top of a breaker panel ? Also what's the 2008 code change mean when multiple NM cable ampacities must be adjusted when passing through wood framing members that are fire or draft-stopped with caulk or sealing foam?Please give an example.
 
The conduit fill rules do not apply to sleeves. Note that you are only permitted to install the NM in a sleeve out of the top of a surface mounted panel.

As far as the derating goes, if you install more than 4 NM cables with #12 conductors, through a hole in a wood framing member that is fire or draft stopped, you will no longer be able to protect the conductors with a 20 amp breaker. With the 5th cable you hit the 50% derating factor turning your #12s into conductors that only have an ampacity of 15 amps.

Note: As "Cow" pointed out in post #12, the conduit fill rule does apply to these sleeves.
 
Last edited:
What's the sizing method for sleeving NM cables in 2" sch.40 pvc conduit ,that's 24" long going in top of a breaker panel ? Also what's the 2008 code change mean when multiple NM cable ampacities must be adjusted when passing through wood framing members that are fire or draft-stopped with caulk or sealing foam?Please give an example.
I believe if there are more than 9 current carrying conductors it has to be derated to 50%. The Idea now seems to be more smaller holes with less wire than 1 large hole with all the wires in it. I think it is easier to drill more 3/4"holes than have to find oddball breakers to connect them to.
 
Chapter nine 60% fill from table 1 notes 4,5 & 9 using the eliptical diameter of cables to figure out the area as if it were a circular cable. That is 60% of the conduits area from table 4. For 2" schedule 40 PVC it would be 1.975 square inches.

As for romexes in fire or draft stopped holes in wood framing you would derate using 310.15(B)(2)(a) an example: four 2-conductor # 12 w/ground type NM cable in a draft stopped hole woul be as follows

4 cables X 2 conductors per cable =8 current carrying conductors
Your allowed to use the 90 degree chart for derating table 310.16 and 334.80. This is 30 amps with an adjustment factor of 70% from 310.15(B)(2)(a).
30X70%=21 amps
Number 12 NM is limited to 20 amps so your OK. But if it was 5 NM cables the adjustmant factor would 50% which would limit your load an overcurrent to 15 amps.

By the time I typed this out you had plenty of responses. I quess two fingers aren't enough.
 
Last edited:
Also what's the 2008 code change mean when multiple NM cable ampacities must be adjusted when passing through wood framing members that are fire or draft-stopped with caulk or sealing foam?Please give an example.

There is interesting wording in this section

Where more than two NM cables containing two or more current-carrying conductors are installed in contact with thermal insulation without maintaining spacing between cables, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(2)(a).

So if I drill a 2" hole thru a bottom plate of a wall many feel that you must derate if more than 2 nm cables are installed in this hole. Suppose I put 12 cables in this hole and separate the cables with a piece of wood or insulation in 3 groups of 4 cables, would I then need to derate to 15 amps in Don's example? According to the wording in this section I would say no since there is spacing between the conductors. Yes? No?
 
Another example of a Code Section out of touch with reality. For NM in a sleeve, I can agree with the derating after so many conductors, but this baloney about the 2" in contact thru a hole in the wood is stupid.

There is so much load diversity in most applications where multiple NM's would be run thru as hole that I am willing to bet there is NO appreciable heat buildup.

And wasn't there a thread heer some time ago where tests were conducted to see if there was any temperature rise in multiple NM's in a fire-stopped hole? I seem to reacll that there was NO appreciable heat buildup found....
 
And wasn't there a thread heer some time ago where tests were conducted to see if there was any temperature rise in multiple NM's in a fire-stopped hole? I seem to reacll that there was NO appreciable heat buildup found....


If I remember correctly that was added to the NEC because testing did find that heat buildup within the fire stopped hole exceeded the temperature limitations of the cable. IMO it's still not likely to do so in the real world.
 
When did a M A get listed as a romex connector ?


It' not ,.. this is an exception to the rule,.. if it were there would be no need for the 18 " .

http://ecmweb.com/nec/code_qa/nec_questions_answered_0201/
902ecmCQfig1.jpg
 
I also found this,.. thought I would share it .


Pre-Ballot Proposals ? June 2007 NFPA 70

_______________________________________________________________________________________________
9-11 Log #3091 NEC-P09
Action: Reject
(312.5)

_______________________________________________________________________________________________

Submitter:
Joseph A. Hertel, Safety and Buildings

Panel Meeting Action: Reject

Panel Statement:
With respect to the three modifications proposed by the submitter, the panel provides the following
response:

1) The 18 inch minimum raceway length was chosen as a distance long enough to provide reasonable
containment of the enclosed cables without specifying a length so long as to require mandatory derating of the cables.
Removal of this length requirement would create the possibility that the enclosure will no longer perform its intended
containment function (A95 ROP ? 9-66a).

2) The exception was written to allow such installations only at the top of the enclosure as the panel noted this
limitation would assure that the outer raceway termination wouldn?t be readily accessible (A98 ROC ? 9-44).

3) The current language not only requires the fitting to remain accessible, but also requires that the enclosure be
surface-mounted.
Adequate closure of the enclosure is dependent upon adequate closure of the raceway. No fittings are designed and
evaluated to close openings around multiple cables as anticipated by the proposal. The lack of suitable fittings presents
the possibility that excess dust, debris, rodents or other pests could enter the enclosure and create a potential
hazardous condition. The existing requirements are intended to mitigate this concern and the level of safety afforded by
those requirements should not be lessened
.

 
M. D.,

Thanks for sharing the pre-ballot proposal from 1997.

For me, this answers some long time questions I have had surrounding the exception to Section 312.5(C).

?Who would have thunk there was actually logic and reasoning, on the part of the CMP, behind the particulars of this exception :) ?