Pre-Ballot Proposals ? June 2007 NFPA 70
_______________________________________________________________________________________________
9-11 Log #3091 NEC-P09 Action: Reject
(312.5)
_______________________________________________________________________________________________
Submitter: Joseph A. Hertel, Safety and Buildings
Panel Meeting Action: Reject
Panel Statement: With respect to the three modifications proposed by the submitter, the panel provides the following
response:
1) The 18 inch minimum raceway length was chosen as a distance long enough to provide reasonable
containment of the enclosed cables without specifying a length so long as to require mandatory derating of the cables.
Removal of this length requirement would create the possibility that the enclosure will no longer perform its intended
containment function (A95 ROP ? 9-66a).
2) The exception was written to allow such installations only at the top of the enclosure as the panel noted this
limitation would assure that the outer raceway termination wouldn?t be readily accessible (A98 ROC ? 9-44).
3) The current language not only requires the fitting to remain accessible, but also requires that the enclosure be
surface-mounted.
Adequate closure of the enclosure is dependent upon adequate closure of the raceway. No fittings are designed and
evaluated to close openings around multiple cables as anticipated by the proposal. The lack of suitable fittings presents
the possibility that excess dust, debris, rodents or other pests could enter the enclosure and create a potential
hazardous condition. The existing requirements are intended to mitigate this concern and the level of safety afforded by
those requirements should not be lessened