howardrichman
Senior Member
On a recent meeting w/a local inspector, we were discussing a service upgrade i'de be doing in the near future, and mentioned if a sub panel is used, and installing a SER cable, i'de have to refer to table 310-16 using the 60C colum. He refered me to art. 334.80 ampacity for NM cable, but also is affected by art.338 for SE cable, but couldn't find it, only permitted and not permitted uses. I've known that Once leaving the main distribution panel; any cable; even a sub panel line when installed, table 310-15(B)(6) is not applicable, and used the 75C colum. According to the inspector, I'de have to use 4/O alum ser for a 150amp sub panel from the main disconnect. I'de thought the sub panel conductors from that main disconnect is still sized as part of the main service.
Any Help;
Howard Richman