Ok a little potential change.

Say I wanted to eliminate the 225A panel( with the 125A, and (2) 60A branch breakers) and use (3) disconnect switches instead could I doo that.
I'd think so but then how would I feed (3) disconnects from a transformer. Run one feed from transformer to a trough, splice, then feed the discos?

Would the disconnects have to be fused? Also 2P3W disconnects?
The disconnects would need to be fused.
You could run a separate feed from the transformer to each disconnect as long as each met the 240.21(C) transformer secondary rules.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Ok a little potential change.

Say I wanted to eliminate the 225A panel( with the 125A, and (2) 60A branch breakers) and use (3) disconnect switches instead could I doo that.
I'd think so but then how would I feed (3) disconnects from a transformer. Run one feed from transformer to a trough, splice, then feed the discos?

Would the disconnects have to be fused? Also 2P3W disconnects?
If I remember correctly the secondary conductors must terminate on an OCPD so the wireway is not an option.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
I gave my breakdown/one line to someone in my office and he responded with below?

P=E x I x 1.73

45000= 208v x I x 1.73

45000/360=I=125 amp 3 ph for trailers with AC & Heat?

I don't follow his logic/calc exactly. I questioned what he meant by 3P for trailers.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I gave my breakdown/one line to someone in my office and he responded with below?

P=E x I x 1.73

45000= 208v x I x 1.73

45000/360=I=125 amp 3 ph for trailers with AC & Heat?

I don't follow his logic/calc exactly. I questioned what he meant by 3P for trailers.
That is the output of a 3Ø, 45 kva transformer.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Ok so with the new scheme of feeding 2P disconnects switches from a 3 phase xfrmr instead of feeding a 3P 4W panel, what would the make up of the cable/wires be from the secondary to the disconnects? 2 phase conductors or 3 phase conductors. Its weird because the xfrm is 3P but the disconnects are 2 pole.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Ok so with the new scheme of feeding 2P disconnects switches from a 3 phase xfrmr instead of feeding a 3P 4W panel, what would the make up of the cable/wires be from the secondary to the disconnects? 2 phase conductors or 3 phase conductors. Its weird because the xfrm is 3P but the disconnects are 2 pole.
The disconnects in those sizes are probably 3 pole but you'll only need to use two poles.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
#1 disconnect to X1-X2 & Neutral XO
#2 disconnect to X2-X3 & XO
#3 disconnect to X1-X3 & X0
all + SSBJ
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
Geniuses ...lol. Thank you. It was just a weird concept to me to have a 3P xfrm but coming off it with only 2 phase conductors.

Right, but keep in mind that you are using all three phases.

You have 3 separate loads, and each of these loads only uses 2 phase conductors.

But you distribute these 3 loads to use all 3 phases.

Jon
 