Thank you. What would the line to line voltage be 120 or 208v? Trying to do the calc.
Once I get the VA then how exactly do I apply that to figure max load on any one phase of xfrmr? Thanks
For this base calc use single phase line to line for each single phase panel.
Example: 125 amp main breaker panel.
125 x .80. = x amps
X amps x line to line (208 v )= x VA
x VA/ 1000 = x KVA.
For this panel using 80% of the main rating method.
Now assign linea to this single phase load.
Example 125 amp panel on lines A and B.
The KVA on line ( phase A) would be x KVA and then the same for Line ( phase B) . Your line to line is 208 volt.
Now do the same for the other two.
Then you simple add up all on each line ( phase) in Descending order.
This would be the KVA for each Line or phase.
Do this first before doing any thing else.
This would be step one the way you working the issue.
Once you post those we move forward if you want to learn how to do from a field perspective.
At this point you can either say move forward for the 45 or step up to a 75.
This is a key step so the one line and panel sch lay out has all information for the field installer to follow. If not you can easily overload the transformer. A simple pic can be used as a inspection tool to sign off on task. Load checks on start up can identify any issue which we will get into later based on your panle pic.
So if you want an easy answer add all panel mains up single phase and size the trans to that . Then no one line will be over loaded. Max KVA on one line and round up on transformer size.
At the end of the day it's your choice. Your name is on it.