The disconnects would need to be fused.Ok a little potential change.
Say I wanted to eliminate the 225A panel( with the 125A, and (2) 60A branch breakers) and use (3) disconnect switches instead could I doo that.
I'd think so but then how would I feed (3) disconnects from a transformer. Run one feed from transformer to a trough, splice, then feed the discos?
Would the disconnects have to be fused? Also 2P3W disconnects?
You could run a separate feed from the transformer to each disconnect as long as each met the 240.21(C) transformer secondary rules.