kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
The garage-light branch circuit is only switched at the house. It does not serve the house (i.e. no loads of the house are powered by this circuit). Hence, 225.30 does not apply.
OK but you have branch circuit conductors installed in the house that do not originate in the house. I would think this would be considered a supply of some type although there is no load in the house and it requires a way to disconnect it. That method of disconnection should be grouped with the disconnect that serves the structure (the service disconnect in this case)
The general idea of any building being served by one service or feeder or grouping multiple disconnects where allowed together is so that you can shut off all power to the building by going to one place to do so.
In cases where other disconnects are allowed there needs to be signs posted to indicate where all disconnects are located as well as what they control.
Why should the mentioned branch circuit be any different?
I still favor using a low voltage control for this application it solves all of these issues