Steviechia2
Senior Member
- Location
- Massachusetts
I h I don't believe article 230 has an exception to allow this. If this is the case what allows the lighting control wiring between 2 buildings supplied by two services?
I agree with you, it doesn't allow it. 230.2 says a building or other structure served shall be supplied by only one service. I know it's only 1 circuit but it is still serving the building with a different service.