Anderman123
So if they were say 7' apart, could you consider them the same structure?That's the building code here. Connected or ten feet apart.
You would be required to join them by at least a breezeway. I believe it has to do with fire spreading.So if they were say 7' apart, could you consider them the same structure?
You can not bond them together if less than 6'. I was thinking if the buildings are that close, run a GEC from garage panel to one of the ground rods. All you would have to do is protect it from damage.If you main building and separate building ground rods are closer than 6ft they are to be bonded together
You can, but they won't qualify as two separate rods.You can not bond them together if less than 6'.
>I believe it has to do with fire spreading.You would be required to join them by at least a breezeway. I believe it has to do with fire spreading.
Kind of stupid isn't it? but at same time you made it become one structure instead of two, technically anyway.>I believe it has to do with fire spreading.
????? Are they trying to make sure the fire spreads?