Me and local inspector have a differance on how the overhead feeders should be and I would like others input. Here is what i did- I ran #4(AL) triplex wire from the house to the garage (2H, 1N) at the disconnect on the garage I have a ground wire #6 that attaches to the ground rod. This is an old garage from the 1940's or 50's there is no other grounding means. This is a 240v 60amp system disconnect outside with a subpanel inside. My inspector failed me because- 1. the overhead wire had no ground wire that ran with the others from the house panel. I added the ground wire to the overhead wires and then I was turned down again because the 3rd wire on the triplex was used as the neutral and was not insulated. In short is the inspector correct in saying that it is required to have the 4th wire a ground and in this case when using the triplex that 3rd cable has to be insulated. I am looking at NEC 250.32. Thanks